31TE Air Conditioning keeps tripping

Post by SJR »

Had a question on a recent issue this past weekend.... A/C unit cools for a few minutes then trips and blows warm (the amps go to zero and the refrigeration units turns off ) Ive read some troubleshooting on this and is points to a possible water flow problem or water pump failure.

was wondering if anyone had any advise on how to check for this and/ or pinpoint what may be wrong. Thanks, any info would be greatly appreciated, system cooled great last weekend.


SJR
TEAGAN II
2006 31' TE
Twin Yanmar 315HP 6-LPAM STP
User avatar
RobS
Gold Member
Gold Member
Posts: 4041
Joined: Wed Oct 03, 2007 6:20 am
Home Port: Center Moriches, NY
Contact:

Re: 31TE Air Conditioning keeps tripping

Post by RobS »

Could be a voltage drop on the shower power supply, have you ruled that out? Does the a/c panel give you a fault code?
Rob S.
"TENACIOUS"
1974 Chris Craft 36' Commander Tournament
Cummins 6BTA 330B's

(Former Owner)
"TOY-RIFIC" 2000 28TE, 6LP, Hull 408

Luck is the residue of good design.
User avatar
DougSea
Gold Member
Gold Member
Posts: 2759
Joined: Tue Jun 13, 2006 9:45 am
Home Port: Safe Harbor - Essex Island Marina, Essex, CT
Location: Essex, Connecticut

Re: 31TE Air Conditioning keeps tripping

Post by DougSea »

Checking a water flow problem is easy, just check the discharge. When your AC is on you should have a solid stream of water flowing from the overboard outlet. Looks like a bilge pump discharge.

If there's not a strong flow you may have a pump or filter problem (have you checked your AC sea strainer?)

You say the unit trips. So I'm asuming the 120 panel breaker does NOT trip, and the blower stays on. Is that right? If so, and you have good water flow, I'd get a technician to look at it.

Good luck!
Doug
Sonny IV
2006 35TE Convertible, Volvo D6-370's
Former owner - Sonny III, 1997 28TE with "The BEAST"
User avatar
SJR
Gold Member
Gold Member
Posts: 64
Joined: Fri Oct 25, 2013 3:05 pm
Home Port: Long Beach NY
Location: Long Beach, NY

Re: 31TE Air Conditioning keeps tripping

Post by SJR »

thanks guys, I checked the the A/C unit and it seems to be in working order. It kicks on and works, then shuts off and just blows with no refrigeration. I cleaned the strainer basket , that seems to be fine, however there is no water flowing overboard. Both the strainer glass and pump seem to be on however reminds me of a pump thats running but not primed. I guess that leaves the water pump? seems no water is making it to the a/c system?

the 120 does not trip and the blower stays on.
TEAGAN II
2006 31' TE
Twin Yanmar 315HP 6-LPAM STP
User avatar
RobS
Gold Member
Gold Member
Posts: 4041
Joined: Wed Oct 03, 2007 6:20 am
Home Port: Center Moriches, NY
Contact:

Re: 31TE Air Conditioning keeps tripping

Post by RobS »

Sounds like she is sucking air and needs to be primed or the pump is shot.
Rob S.
"TENACIOUS"
1974 Chris Craft 36' Commander Tournament
Cummins 6BTA 330B's

(Former Owner)
"TOY-RIFIC" 2000 28TE, 6LP, Hull 408

Luck is the residue of good design.
User avatar
kathylsails
Gold Member
Gold Member
Posts: 209
Joined: Wed May 05, 2010 2:32 pm
Home Port: New Bern, NC
Location: New Bern, NC

Re: 31TE Air Conditioning keeps tripping

Post by kathylsails »

We had that problem with KP Duty a couple of years ago. Even though the water pump was running, the through hull valve was not opening. Replacing the valve solved the problem.
"KP Duty" Albin 30 FC
Marcy K
Gold Member
Gold Member
Posts: 146
Joined: Sun Oct 11, 2009 10:06 pm
Home Port: Cape Cod MA

Re: 31TE Air Conditioning keeps tripping

Post by Marcy K »

We had the same problem last summer. It turned out that the strainer had an air leak and wouldn't/couldn't hold a prime. After taking the strainer apart and cleaning it, we primed it and sealed the threaded ends. The heater/AC has worked perfectly since. Hope its that easy!

Marcy K
A 34 Paumanok 1986
Falmouth, MA
Marcy K
A 34 Paumanok 1986
Cape Cod MA
Nancy
Gold Member
Gold Member
Posts: 1807
Joined: Thu Apr 23, 2009 8:41 pm
Home Port: Lake Champlain

Re: 31TE Air Conditioning keeps tripping

Post by Nancy »

We have to prime our unit every spring. And if we haul mid-season and leave the through-hull open, we have to prime again. Symptoms are exactly as you describe.
Take off the first hose coming out of the pump and turn on the AC unit. If water comes out of the hose, the pump is fine.
Turn off the AC unit.
Put the hose back on.
Turn on the AC unit. If water comes out the through-hull fitting, you're finished. If not, turn off the AC unit.
Take off the inlet hose at the AC unit and turn on the AC unit. Water should come out the hose. Turn off the unit. Put the hose back on. (If water doesn't come out of the hose, you need more help than I can give you. :D )
Turn on the AC unit. If water comes out the through-hull fitting, you're finished. If not, turn off the AC unit.
Take off the outlet hose at the AC unit and turn on the AC unit. If water comes out the hose, turn off the unit. Put the hose back on.
Turn on the AC unit. If water comes out the through-hull fitting, you're finished. If it doesn't, the problem is over my head.

There might be more than one way to do this - I don't know - I'm not really an HVAC girl. This is what works for me.

Good luck!
Nancy
2005 Albin 35CB
Yanmar 6LYA-STP 370
Valentine

Former boats
1995 Albin 28TE, Cummins 6BTA5.9 250, 2012-2022
1978 Trojan F32, 1998-2012
1983 Grady White 241 Weekender, 1988-1997
1980 Wellcraft 192 Classic, 1983-1987
N4QC
Gold Member
Gold Member
Posts: 215
Joined: Tue Aug 15, 2006 8:56 pm
Location: Tampa Bay

Re: 31TE Air Conditioning keeps tripping

Post by N4QC »

The easiest way for me to reinitiate the prime for the AC system on my vessel is to take a water hose with a nozzle and back flush the cooling system. With the AC off, direct the nozzle into the AC discharge port on the hull. Turn water on for a minute or so. Turn off water - turn on AC. If after two or three failed attempts I would suspect the pump. This of course assumes that the previous suggestions about the clean filter, the filter housing, valves and air sources into the system have been addressed .

In checking out the pump you may be able to verify that the impeller is free to spin by removing the outlet hose and outlet connector from the pump. This would give you access to the impeller whereby you should be able to spin it with a finger. Make sure that the power to the pump is turned off first.

Access to the pump is another matter…

Happy trouble shooting,
Joe
Albin Getaway
"LabTime"
User avatar
DougSea
Gold Member
Gold Member
Posts: 2759
Joined: Tue Jun 13, 2006 9:45 am
Home Port: Safe Harbor - Essex Island Marina, Essex, CT
Location: Essex, Connecticut

Re: 31TE Air Conditioning keeps tripping

Post by DougSea »

Hey SJR - as you can see from the above many suspect a priming issue. Just in case you're not aware, A/C pumps are NOT self priming. They SHOULD be installed below the waterline, but aren't always. There are some great suggestions above for checking/establishing a prime.

Based on your reply above, lack of water flow is certainly your issue. With luck it's a lack of prime or an air leak, at worst you need to replace your pump. Not a terrible job (depending on the pump location!) and a quick fix.
Doug
Sonny IV
2006 35TE Convertible, Volvo D6-370's
Former owner - Sonny III, 1997 28TE with "The BEAST"
User avatar
JackK
Gold Member
Gold Member
Posts: 465
Joined: Fri Jun 30, 2006 8:14 am
Home Port: Portsmouth, Rhode Island
Location: Plainville, MA

Re: 31TE Air Conditioning keeps tripping

Post by JackK »

What they said ... priming the a/c pump.

Mine is a proverbial pain in the neck. It is not below the waterline and every year I have to fight with it during commissioning. The method that has worked the best so far is - (a) shut the a/c seacock, (b) pull the hose from the seacock by loosening the hose clamps, (d) turn on a freshwater hose to a moderate flow, (d) while forcing water into the a/c hose have an assistant turn on the a/c. and (e) once the flow is established (wait for a couple of minutes), quickly replace the hose and open the seacock. Make sure you tighten up the hose clamps when finished.

I have had to repeat the above process several times depending on how fast I can get the hose back on the seacock. I keep meaning to relocate the pump but since it has never lost prime once I get it going for the season, it remains low on the to-do list.

Jack
former boat .. 2003 28 TE Flushdeck Dogonit
User avatar
DougSea
Gold Member
Gold Member
Posts: 2759
Joined: Tue Jun 13, 2006 9:45 am
Home Port: Safe Harbor - Essex Island Marina, Essex, CT
Location: Essex, Connecticut

Re: 31TE Air Conditioning keeps tripping

Post by DougSea »

Jack - On Sonny III I had the same challenge. Pump was just at the waterline and would not self prime. I put a tee into the raw water wash-down feed just behind the bulkhead where it fed the hose bib. Took a feed off of the tee, ran that to a valve and then a tee in the A/C raw water line, between the pump and the thru hull. To prime the system I just turned on the wash-down pump, opened the valve, and voila! Cost was 2 tees, a valve, and some hose. Convenience was priceless!

Makes winterizing a breeze as well.
Doug
Sonny IV
2006 35TE Convertible, Volvo D6-370's
Former owner - Sonny III, 1997 28TE with "The BEAST"
User avatar
RobS
Gold Member
Gold Member
Posts: 4041
Joined: Wed Oct 03, 2007 6:20 am
Home Port: Center Moriches, NY
Contact:

Re: 31TE Air Conditioning keeps tripping

Post by RobS »

Suprised to see how many struggle with the priming of the pump and have never added a freshwater flush or a priming connection. Doug's priming connection is a great solution but the freshwater connection (flush) I did in T-R is even better. Remember the a/c is subjected to the same ill effects of seawater as the cooling loop on the engine.

You can prime the a/c but you can also flush it with freshwater when not in use and it makes winterizing a snap - close the seacock, open the freshwater connection valve and wait for pink to come out of the side of the boat.

With the water heater right there it was simple to "T" into the cold water supply.

Never touch a hose clamp again..
You do not have the required permissions to view the files attached to this post. To view images, please register for a free account.
Rob S.
"TENACIOUS"
1974 Chris Craft 36' Commander Tournament
Cummins 6BTA 330B's

(Former Owner)
"TOY-RIFIC" 2000 28TE, 6LP, Hull 408

Luck is the residue of good design.
User avatar
SJR
Gold Member
Gold Member
Posts: 64
Joined: Fri Oct 25, 2013 3:05 pm
Home Port: Long Beach NY
Location: Long Beach, NY

Re: 31TE Air Conditioning keeps tripping

Post by SJR »

Awesome info, thanks to all. It is my first season with Teagan II, and was on the fence as to call a tech, hopefully I can get it primed myself. Learned allot already. The pump is directly below the Helm, once I get a quick break from work Im all over it. I love the the Tee and fresh water flush, that will be on the off season list.
TEAGAN II
2006 31' TE
Twin Yanmar 315HP 6-LPAM STP
Nancy
Gold Member
Gold Member
Posts: 1807
Joined: Thu Apr 23, 2009 8:41 pm
Home Port: Lake Champlain

Re: 31TE Air Conditioning keeps tripping

Post by Nancy »

SJR wrote:hopefully I can get it primed myself.
Hey, if I can do it, anyone can. :shock:

Our pump is below the waterline, but the AC unit is uphill from there. In theory, it should prime itself, but it doesn't. Also, the shooting water in the through-hull trick doesn't work for me.